RDREC (SFB 52) is a PLC-internal instruction that runs on the PLC CPU itself -- it cannot be invoked remotely via the S7 communication protocol. The correct approach is to have PLC logic execute RDREC and store the results in a global data block, then use client.db_read() to retrieve that data remotely.